The collective experience and technical knowledge of this group is requested to provide remedial suggestions to answer the following question: How does one mitigate moisture migration issues when a vapor retarder is absent or defective?
Scenario:
A +10-year old community swimming pool facility (located in Northern Virginia) has moisture and ventilation issues in a large attic. The roof is of a hip design with asphalt shingles. The roof structure is supported by a wood truss system supplemented by a piggy back truss located on top of the primary (lower) truss with a horizontal OSB diaphragm located about mid-point of the vertical height of the attic space where the two trusses meet. The attic has three vertical draft-stopping partitions creating compartments (two at approximately 4,000 SF and a one at approximately 1,000 SF).
The facility houses an L-shaped swimming pool (approximately 5,000 SF in size) with a coffered ceiling with a 6-mil poly vapor retarder and unfaced, fiberglass batt/blanket insulation (R-19). The vapor retarder is compromised with numerous penetrations and does not have properly taped joints or overlaps.
The remainder of the facility houses locker rooms, fitness areas, dance studio, and several mechanical/pool equipment rooms. These spaces have no vapor retarder above their respective ceilings but do have unfaced fiberglass blanket/batt insulation (R-19) suspended about 3’ to 5’ above the ceilings of these spaces. This plane of insulation is so completely compromised with large gaps and missing insulation that it is useless as a thermal envelope. The net effect of the above scenario is that there are three levels of attic: upper and lower truss spaces separated by the horizontal diaphragm and the horizontal plane of thermal insulation (as defective as it is) located below the trusses.
There are continuous soffit vents that appear to be open and effective (very good) but there are a grossly inadequate supply of ridge vents in the upper portions of the attic (very bad). There is another complicating factor with heat producing mechanical equipment located within the attic space.
The scope of work includes replacement HVAC equipment including a properly designed dehumidification and temperature (water and air) control system for the interior space for the pool.
Design Intent:
Remodel the attic such as to produce a properly designed single attic with a properly functioning passively ventilated attic.
Remedial Actions Scheduled to be Taken:
The following remedial actions are currently proposed:
- Installation of additional ridge vents supplemented by multiple off-ridge vents (typical of those used in Florida residential construction) as necessary to achieve a balanced (incoming and exhausted) passive ventilation system.
- Removal of at least 50% of the horizontal OSB diaphragm (subject to acceptance of the structural engineer).
- Relocation of the unfaced fiberglass insulation from its suspended position down to the top side of the ceiling systems (suspended GWB or suspended acoustical lay-in panels) without the installation of a vapor retarder (just not possible under the existing conditions).
So back to my original question, How does one mitigate moisture migration issues when a vapor retarder is absent or defective? which is directed to item #3 above. Can an excessive application of fiberglass insulation (supplemented by loose insulation), say R-38, retard the flow of moisture to an acceptable level?
My apologies for posting such a long thread question. I tried to make it shorter but there were just too many issues (some not presented).