I spoke with someone at ICC regarding any required flame spread or smoke-developed index for PVC drywall trim, specifically related to a “new” product that can be as much as 3.5 inches high above the floor.
The gentleman at ICC was of the opinion that “trim” is “trim” and that drywall trim must comply with IBC 806.7 (Class C when tested in accordance with ASTM E84.)
Of course, drywall trim does not come in the test sample size required by ASTM E84 (20 to 24 inches wide and 24 feet long), but that did not seem to be of any concern to the gentleman with ICC.
I could only fine one manufacture of PVC drywall trim that listed ASTM E84 testing. They told me they had no idea why they included that information, and would not have any test reports to support the data.
Rigid PVC will have a flame spread index (FSI) less than 25, so it would be considered a Class A finish. Materials with low FSIs will generally have low smoke developed indices (SDI).
I looked to see if ASTM D3678, Standard Specification for Rigid Poly(Vinyl Chloride) (PVC) Interior-Profile Extrusions, includes the ASTM E84 test, but it does not.
Just think, we put PVC on the roofs of buildings (which is flexible and has a lower FSI) without much of an issue (even though roofing is tested differently), so it would reason that the rigid trim for gypsum board would have an equal or better performance than roofing.
My interest was in a specific product, but the ICC guy did not think it made any difference if it was PVC drywall corner bead or any other type of PVC drywall trim.
Based on Ron Gerens statements, I cant help but wonder if someone else had answered the ICC telephone, I would have received a different opinion.
Per ASTM C1047, PVC trim must comply with ASTM D3678, Class II or III, which requires PVC extrusions to comply with ASTM D1784, the standard Ron referenced. ASTM D1784’s reference test for flammability is ASTM D635, not ASTM E84.
However, based on the link Ron provided, it appears that rigid PVC of any size or profile would meet the requirements if IBC 806.7, whether or not required for gypsum board PVC accessories.
I think an argument could be made for corner bead not being “…decorative or protective…”, i.e., nothing like/similar to moldings, chair rails, baseboards, etc. as examples cited in IBC? Corner bead is neither “interior…finish” as it is not exposed per Chp 2 definitions for “interior wall and ceiling finish”?
I think your “mistake” is calling it “trim”; correct nomenclature is “corner bead”…embedded in wall assembly…and not a surface-applied decoration?
Corner bead is “protective”–it protects the external corner of a gypsum board wall from damage and is specifically mentioned in ASTM C840, “external corners shall be protected with a metal corner bead or other suitable type of corner protection…”
As for not calling it trim, well, ASTM C840 refers to metal and PVC accessories (including corner bead) as “trim and casings.”
Although corner bead is covered by a coating of joint compound, some PVC accessories are exposed.
I understand that ICC’s response is an opinion and not an official committee interpretation, and the response from another staff member may have resulted in a different opinion. Calling corner bead “trim” by IBC definition is splitting hairs, but the fact remains, whether “trim” or not, the material complies with IBC’s requirements for “trim.”