I would appreciate a generic drawing name for cold-formed metal channels with flange edges returned toward web and with 9/16 inch wide slotted holes in webs at 2 inch centers, with rust inhibiting acrylic enamel paint electro-deposited and baked; single channel and double, back-to-back channel. Same as manufactured by Unistrut Corporation or Power-Strut.
While this standard, which I had not seen before, helps bring uniformity to these systems it may be that Wayne’s concerns are not fully answered.
If you simply want to specify that a Metal Framing System is to be used that will be designed and detailed by the Contractor it is probably adequate.
There does not appear to be a generic notation for calling out specific strut channels. There are variations of geometry and the layout of the holes punched in the channels that are sometimes critical. I have handled this by using the Unistrut notation. There exist cross references that claim to give you the notation that is used by the other manufacturers.
Many of the fittings are specific to a particular manufacture and thus if you or your consultants are designing the system, you will have to call them out using the manufacturers designation.
I am not sure that the “standaed” is fully maturee thus the designer could have to reference other sandards to. This may not be a problem in many instances because the channels themselves, ut not the fasteners, are covered by the AISI standard.
Notwithstanding everyone’s postings, what I have thought is important, from spec standpoint, is metal (or material) and finish be appropriate for specific application environment…whether it be aluminum, fiberglass, carbon or stainless steels, painted, zinc-plated, pre-galv, or HDG (which might be limited to thicker gages?)
These miscellaneous channels seem to end up being treated in the same way that many fasteners are: “use fasteners.” In both cases, we assume that the appropriate items are selected by the contractor. If the above-ceiling mounted transformer doesn’t come crashing down, then it was a good assumption.
It would be good to consider requiring calculations with shop drawing submittals, or even a delegated design submittal, if you are supporting big stuff.
Statements such as “use fasteners” are troublesome because they may give others the impression that you have evaluated the loads when you have not. These statements are often an indication that somebody has gotten lazy and dropped the ball.
In these situations you should either formally assign design responsibility to the Contractor or accept responsibility for the design or lack of design. This does not mean that all situations must be formally engineered but it means that you have considered the issue and have decided that if you were to do the formal calculations that it would be safe.
What qualifies as “big stuff” can vary depending on the configuration of the framing system.
One more consideration would be to include a statement such as:
“Once contractor has selected the metal framing manufacturer, all components of the system shall be from a the same manufacturer”