The contractor installed plywood for backing and shear on our project. Now we come to find out that the wood needs to be fire treated. Does anybody know a field applied fire treatment for wood to make it fire rated?

What building code is in effect, and what is the construction type?

IBC 2003 Type II B construction

Yes, fire-retardant-treated wood is required.

It is possible that you may have under-estimated the allowable area; therefore, you might be able to drop down to a Type III construction. Let’s see if we can work towards that:

  1. What are the occupancies?
  2. Did you go separated or nonseparated uses?
  3. What is the floor area of the largest floor?
  4. How many stories (not counting basements)?
  5. Is a sprinkler system installed throughout?
  6. What percentage of the building’s perimeter has a fire separation distance (distance from property line, center of road, imaginary line, etc.) greater than 20 feet?

I recently had a client that selected intumescent coatings for application on existing wood to comply with requirements for non-combustability. We spec’d products by Flame Control Coatings LLC, Niagara Falls NY (716-282-1399).

Ronald,

I appreciate your help but think that we are too far down the line to change construction type classification. I proposed the question to the project manager anyway.

Jeffrey,

I have investigated all sorts of coatings. They reduce the surface flame spread but not the burning characteristics of the wood itself. This may not word because plywood is not an exposed finish but instead will be buried in the wall and will have untreated back side, edges and inside.

We may have end up having to remove the untreated plywood and install treated plywood or install a layer of 5/8 inch Type X gypsum board. If we go the gypsum board route we will have to redetail door frames and transitions.

Actually, it’s never too late to change. The building can not be classified any higher than the type for which it meets the minimum requirements based on occupancy (Section 602.1.1). In otherwords, if it can be classified as Type III, A or B, construction, then you can not be required to comply with the more restrictive requirements of a higher construction type.

If, during construction, the jurisdiction can make you add stuff that they missed during plan review, they should also allow you to reduce the classification if you do find that it does comply with those minimum requirements.

Contrary to what I just said above, I think that I have found the product!

FireFree 88

Has anybody had any experience with this product?