We specified unfaced batt insulation for interior partitions of an apartment project, some walls are rated, some are not; the GC wants to use faced fiberglass batt insulation, because he claims there will be a savings in labor time. This is a JM product and the unfaced insulation meets flame spread requirements of the spec and ASTM E94, the faced insulation does not. I refused to approve it, however the architect has asked me to reconsider…I have no idea why?
If there is no concern about vapor barrier, what is the difference between using faced and unfaced batt insulation in an interior partition other than flame spread?
In fire-rated partitions, the type of insulation used in the tested assembly must be used.
In non-fire-rated partitions, even if faced insulation is used, if the joints between batts are not taped, the facings will effectively not be a vapor retarder.
Is it wood framing?
Kraft faced insulation has stapling tabs for quick attachment to wood framing.
Unfaced insulation is friction fit vertically. Horizontal applications may require wire rod, chicken wire or wire to hold it in place.