What is the best material to fabricate a downspout from that is embedded in a concrete column? In this application is it still considered a downspout?
Jerome,
I would say PVC that can be encased in concrete such as a conduit.
Depending on what it connects to, it could be considered plumbing.
Be sure that this is coordinated with the structural engineer. This is the sort of thing that an Architect will show on the architectural drawings without coordinating it with the structural engineer. The pipe, especially where it enters or exits the column, could displace critical reinforcement.
Do not be surprised if the structural engineer says no can do unless significant changes are made.
Party pooper!
Actually I think Peter is correct. You should probably talk with your plumbing designer as well as to the best way to specify this.
It may not be plumbing by code, but I’d treat it as if it was for design purposes. There’s no real money to save by going cheaper.