This forum has discussed NFPA 285 requirements for plastic insulation and an article from the ICC website clearly mentions that the assembly as a whole be tested - not something similar. see this link for the previously discussion http://discus.4specs.com/discus/messages/24/5477.html
Now a new wrinkle as sprung up. It appears that air barriers are considered a portion of the assembly as is the insulation, gypsum sheathing and in my case MCM panels.
HOW oh HOW are we building buildings without a constant stream of assemblies being trotted off to testing labs for the 30K NFPA 285 test for your PARTICULAR assembly?
This question came up last week on a job. The MCM manufacturer stated that they felt our vapor impermeable membrane would contribute to a failure in the system when tested and were anxious about its choice. They stated that they knew of several Vapor Permeable products on the other hand that would be OK.
I was at a loss. The NFPA 285 requirement has been in the IBC since 2000.
Why had this never come up before?
Have project architects been receiving these test results? They have been required in all of my specs since 2008(ish) (Thank you Speclink you have included this as standard language) Masterspec does NOT reference this test only ASTM E 84 and E 119
What is the difference, in a fire, between vapor permeable and impermeable?
How are air barriers or other products tested separately from the whole assembly?
Will the contractor/manufacturer have to test (at a cost of $30,000 each time) the MCM exterior wall assembly every time a different air barrier or insulation is selected?
There are 15 to 20 different MCM systems, tens of air barriers, hundreds of insulation brand names and products, resulting in thousands of possible combinations!
I got out NFPA 285 and read thru it. The test standard states in section 5.7 that
The test specimen shall be constructed and secured using fastening and construction details representative of actual field installation as specified by the manufacturerjoints or seams representative of standard construction practicesshall be incorporated
I called NFPA and ask them what they thought. They agreed with me that testing every possible combination was never the intent of the standard but that the system does have to be tested.
The exterior assembly consists of the metal studs, the gypsum sheathing, the air barrier, any accessory tapes and sealants, the outboard insulation, the MCM framing system, the MCM panels. The sheathing, air barrier, and insulation are parts of the assembly (not joints and seals) that would logically need to be tested. The sheathing for our buildings is always Type X Gypsum sheathing has been part of these tests historically and should not be an issue.
Exterior insulation and the air barrier are two additional elements in the assembly that can affect test results.
I called my local Carlisle rep (their impermeable product is scheduled for the building at this time) He stated that he had just heard of this issue and the company had developed a new impermeable product that would be OK in the test assembly. Their new product literature states that the product complies with NFPA 285 what does that mean? He is getting the test or engineering reports for me at this time to clarify this.
I called the rep for WR Grace and he had not heard of this issue either but with a little digging found a letter that stated that Grace perm-a-barrier and XPS insulation (Extruded Polystyrene) should be fine when testing assemblies per NFPA 285. Again what assemblies were tested?
The Local reps for MCM panels were similarly in the dark and both are investigating.
Im still investigating and Im now broadening my reach.
WHAT are you folks doing?.
Here are the choices I have at the moment:
- Stop using MCM panels
- Specify only those air barriers approved by the MCM manufacturer (with test results required, of course)
- Specify air barriers that will not generate flame or elevate the wall temperature beyond those listed in NFPA 285. Then make assumptions about possible test results and place the burden of testing upon the MCM fabricator (and add 30,000 dollars to your project cost.)
- Make the Contractor submit similar tested systems to the Authority Having Jurisdiction AHJ for the hope of approval without new testing.