Moisture Mitagation Coating

I also have considered moisture mitigation to be entirely a schedule issue with only a few exceptions. In the Northwest, I’ve been told that concrete cures about 1/2 inch a month in the 6 cooler months and about 1 inch a month in the 6 warmer months. That means that an 8 inch thick slab will cure in the course of the year if it is kept ventilated and unsealed. in Southern California I’ve been told 1 inch per month for nearly the entire year. I’ve also been told that in South Carolina near the coast, the time is “never”.

If you are doing a big box store with a 10 inch slab and want it open in 3 months, it will not cure enough for a finish floor in that amount of time. Good thing that polished slabs are in style.

This assumes that the building is more or less enclosed, and ventilated and there are no open water lines draining onto the slab. (the last time someone said that they “couldn’t meet the moisture numbers”. )

What I learned in school many, many moons ago, is that concrete will continue to cure indefinitely as long as there is unhydrated cement and water to hydrate the cement. For a relatively standard mix, concrete has cured to about 90% of its design limit after 28 days, but if you were to test it a year later, it may have reached its design limit, probably a bit more.

The problem is the water that can never be used for curing and must evaporate. Evaporation must be controlled for other reasons, but only about 1/2 of the water we put into concrete will ever be used for curing. I have begun to wonder if this is the water that needs to be dealt with, and I also wonder if there is any downside to sealing in that amount of water by putting a moisture mitigation membrane down.

I’ll add a few points:

Without a doubt, the best reference I’ve seen on this issue is ACI’s publication “302.2R-06: Guide for Concrete Slabs that Receive Moisture-Sensitive Flooring Materials.” It is well worth the $42 to $70 (depending on whether you’re a member.) This is a must-have for every specifier.

I agree that means and methods can go a long way to reducing slab moisture from water in the concrete mix, or from conditions that add water to the slab during drying (such as using leaky hoses or not properly enclosing the building). I like the idea of requiring the contractor to take such means and methods as necessary to dry out the slab -OR- in the alternative, use a (specified) moisture mitigation membrane. I’ve never had a chance to fully test this procedure, though I’ve specified it.

Sometimes even old, existing slabs have moisture problems. This clearly is the responsibility of the owner, but it can be predicted if testing is done well in advance, during design.

Having the flooring contractors’ tests as the only ones, or first ones, is a recipe for disaster because they will do the test maybe one week before they start. (Likely when the contractor calls them and says “you have to start Monday or we’ll be behind schedule.”) Plus, you may have multiple flooring subs on one job. If the first test is done at this late date, options to dry the slab are no longer viable, leaving only a membrane as the solution. Slabs have to be tested on an ongoing basis soon after placement.

There are a number of variables that affect the need for a membrane. 1) Some areas of the same building may be problematic and others may not be, for reasons that can’t be fully predicted. 2) Some areas may need to be done on greener slabs than others depending on the work sequence and required completion dates. 2) Some materials are more sensitive to moisture than others. 3) Some areas may have been better protected against wetting during construction than others.

While the concrete strength may be high at 28 days the amount of availible water is not necessarily low. Water content is closly related to shrinkage of the concrete and probably less than 30% of the long term shrinkage occurs by 28 days.

The use of fly ash and other green strategies can result in concrete that needs 56 days to reach the specified strength.

We have reduced the amount of water by the use of admixtures but much of the water is still needed to be able to place the concrete properly. Do not expect a magic solution that produces dry concrete.

Rather than seeing the problem as a problem with the concrete we should realize that concrete is what it is and can only be changed so much. Two other approaches include using another type of floor construction or change the floor covering system.