# manufactured roof edges - code requirement or not?

**URL:** <https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188>\
**Category:** Archive - Specifications Discussions #4\
**Created:** [February 10, 2009, 8:45pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188 "2009-02-10T20:45:46Z")\
**Posts on this page:** 6\
**Page:** 2

<div class="post-metadata">

**Author:** ![Rliebing](https://avatars.discourse-cdn.com/v4/letter/r/c57346/32.png) [@Rliebing](https://forum.4specs.com/u/Rliebing)\
**Post date:** [February 12, 2009, 1:16pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188/21 "2009-02-12T13:16:31Z")

</div>

Isn’t it reasonable if not true that you have a better chance of getting properly tested work out of a metal edge manufacturer [an engineered/extruded system] than from a local sheet metal fabricator’s shop? And after all isn’t that what is required, really, and with relatively little impact on project cost.

Also we have been advised that on FM insured projects you must use the FM standard 1-90 and not ES-1.

---

<div class="post-metadata">

**Author:** ![bunzick](https://avatars.discourse-cdn.com/v4/letter/b/a587f6/32.png) [@bunzick](https://forum.4specs.com/u/bunzick)\
**Post date:** [February 12, 2009, 1:57pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188/22 "2009-02-12T13:57:05Z")

</div>

Please, all, take a look at the actual test. It requires no apparatus more complicated than a stand and a spring scale capable of weighing 150 lb. Test size is 12 inches long. I can’t imagine that such a test would be “prohibitively expensive.”

By the way, ES-1 is more than a test, it is a “Wind Design Standard for Edge Systems…” so it includes design criteria and methodology as well as a few test methods.

---

<div class="post-metadata">

**Author:** ![tsugaguy](https://yyz1.discourse-cdn.com/flex047/user_avatar/forum.4specs.com/tsugaguy/32/214_2.png) [@tsugaguy](https://forum.4specs.com/u/tsugaguy)\
**Post date:** [February 12, 2009, 2:22pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188/23 "2009-02-12T14:22:07Z")

</div>

John: “prohibitively expensive” - Perhaps that is what they say when it wasn’t in their bid.

But if it is in the spec, should be no matter, right? What if Owner & GC have VE’d it out? Can they, or does code truly require reports?

---

<div class="post-metadata">

**Author:** ![specman](https://yyz1.discourse-cdn.com/flex047/user_avatar/forum.4specs.com/specman/32/222_2.png) [@specman](https://forum.4specs.com/u/specman)\
**Post date:** [February 12, 2009, 4:51pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188/24 "2009-02-12T16:51:54Z")

</div>

Keep in mind that the fire-resistive requirements in the IBC (Section 703.2) also state that the rating be “determined in accordance with the test procedures set forth in ASTM E 119…”

How many gypsum board installers and framing contractors have the fire-resistive wall assemblies they build tested even it complies with a tested UL assembly?

I feel the NRCA tested assemblies are not unlike UL-tested fire-resistive assemblies: if you design and install the assembly as tested, then having an actual test is not necessary.

---

<div class="post-metadata">

**Author:** ![bunzick](https://avatars.discourse-cdn.com/v4/letter/b/a587f6/32.png) [@bunzick](https://forum.4specs.com/u/bunzick)\
**Post date:** [February 12, 2009, 7:09pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188/25 "2009-02-12T19:09:56Z")

</div>

Chris: IMHO It cannot be VE’d out any more than a rated partition, but that does not automatically mean that a report is required.

---

<div class="post-metadata">

**Author:** ![Phil\_Kabza](https://avatars.discourse-cdn.com/v4/letter/p/6f9a4e/32.png) [@Phil\_Kabza](https://forum.4specs.com/u/Phil_Kabza)\
**Post date:** [February 12, 2009, 7:49pm UTC](https://forum.4specs.com/t/manufactured-roof-edges-code-requirement-or-not/1188/26 "2009-02-12T19:49:19Z")

</div>

Resources on this page may be useful to Forum members: [http://www.nrca.net/rp/technical/details/itslisting.aspx](http://www.nrca.net/rp/technical/details/itslisting.aspx)

Perhaps as we get more experience with this requirement and with how our AHJs treat it, we can revisit this discussion.